**Author:** ![Christophe\_C](https://avatars.discourse-cdn.com/v4/letter/c/FF8800/32.png) [@Christophe\_C](https://community.br-automation.com/u/Christophe_C)\
**Post date:** [March 10, 2026, 4:04pm UTC](https://community.br-automation.com/t/1067375820-temperature-sensor-not-connected-or-destroyed-temperature-1e-06-for-acopos-p3-drive/10447/1 "2026-03-10T16:04:26Z")

</div>

Hi everyone,

I wanted to share a bit of helpful information about a possible cause of the **“Temperature sensor not connected or destroyed”** error.

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/7/7f3afdfbbb69250e5cf4557aec803edfc2282f80.png)  
This error has a couple of resolution suggestion

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/3/3a3dfc54acf8cca84421499cc3ad960219879a92.png)  
This error typically comes with a few suggested resolutions, but I think one important potential cause is missing. **Setting the controller mode to Voltage/Frequency control on a P3 can trigger this error.**

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/d/d81454abf5d01430670324013d3161f076685742.png)  
It’s a simple issue, but if—like me—you assume the problem is related to a temperature sensor or the temperature model (as the error message suggests), it’s easy to overlook this by focusing only on temperature‑related parameters.

Switching the controller mode back to **Position Control** should resolve the issue.

Hopefully this helps save you some time and prevents you from troubleshooting in the wrong area if you encounter the same situation.

---

<div class="post-metadata">

**Author:** ![kovarj](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/kovarj/32/537_2.png) [@kovarj](https://community.br-automation.com/u/kovarj)\
**Post date:** [March 11, 2026, 7:19am UTC](https://community.br-automation.com/t/1067375820-temperature-sensor-not-connected-or-destroyed-temperature-1e-06-for-acopos-p3-drive/10447/2 "2026-03-11T07:19:06Z")

</div>

thanks for sharing 🙂