Acopos 1090 - Red light lights up constantly when plugged on machine

Dear forum members,

I have an ACOPOS 1090 servo drive which is working fine when testing on the workbench. It accepts the configuration just fine and starts up normally.

When plugged on the machine though, the red LED lights up constantly indicating an error during boot according to the respective page of the manual.

The machine works fine after replacing the drive with a new one.

Kindly tell me what could be the cause of the problem.

Details on the hardware:

Machine CPU: IP161

Testbench CPU: Automation PC with AREmb

Drive: ACOPOS 1090

Interface: CAN

Thank you in advance for your support!

Hard to say. Since the problem is fixed after drive replacement, it can be signed that there is a hardware problem. It can be the drive itself, the AC114 CAN card, cable, or resistor. The easiest way to determine the cause of the issue is component swapping, from my point of view. But leaving space for motion experts here to share their thoughts.
:slight_smile:

No motion expert :wink:

But I just wanted to mention, that the testbench PLC is a APC (SG4 system), while the machine PLC is a IP161 (SG3 system). In principle and as long as the software components like ACP10 and so on are the same, it should work anyway… but if they aren’t the same, I could at least imagine that there’s “something newer / different” in the testbench then in the machine, and that there could be a combinatoric issue with different drive operating system versions + pre-installed firmware versions (e.g. of the CAN interface) and/or with the availability of a suitable ACP10 version in the IP161 …
… I have a vague recollection that on SG3 PLCs, depending on the overall project content, sometimes there was not enough free PLC memory to store the ACP10 module in the PLC memory. Then for sure the ACP10 can’t be spooled by the PLC over network to the drive… and if the version stored in the drives EEPROM don’t fits to what the PLC wants/needs but the APC10 cannot be up-/downgraded by the PLC, I could imagine some “deadlock situation” … honestly spoken I can’t remember how the LED status were in such a case, I just wanted to mention the difference between the testbench and the machine.

Best regards!

The CAN card and cable have not been replaced, they are the original ones :wink: . Swapping the drive to a different position did not help either.

Only replacement solved the problem, meaning that it is definetely an issue from the drive itself.

Thank you for your answer, I am truly grateful!

Spyros

Good morning Alexander!

Thank you for sharing deeper technical information on this matter! What you mentioned is very interesting.

This can very well be our case here. As far as I know, it is not possible to retrieve the configuration from an ACP10 system since they are meant to be configured with every power up of the system, if differences are detected by the PLC or IPC of course.

It would be useful to know how it is possible to configure an ACP 10 drive to work with a SG3 PLC with insufficient memory.

Have a nice weekend!

You can swap only the CAN card; it could be that the drive itself is okay and only the card has an issue. The question is, how much time (your time is cost) would you like to spend on the issue? You have replaced the drive and the problem is solved. All good. How much time do you want to spend on this issue? If it is a hardware issue, you probably cannot fix it by yourself, so you can either send it to the repair department or throw it away.

The new drive came with no interface cards, the cards used for CAN and resolver are the original ones, this is what I meant before :slight_smile: . I apologize if this was not clear.

ahaaa :wink: now it is clear.

Hi,

unfortunately I don’t have any practical experience in that direction.
But not failing to provide an answer:
I assume the best way would be (the concrete way to do depends a bit on the Automation Studio versions used, so I can’t describe it in detail but just as common process):

  • identify the motion software versions (ACP10) used in the IP161 by examining the IP161 project
  • check if these versions are available also for the testbench configuration
  • if yes, create a configuration / project using that versions on the testbench setup, and check how the system works there - if the drive do some motion / firmware upgrade, you could try after that how the system behaves at the other machine.

Best regards!

Hi @Kavourdistiri what is status of your issue? can you update us and help us keep community organized?

closed by moderator: AI generated summary:

Spyros Georgiadis reports that an ACOPOS 1090 servo drive functions correctly on a workbench testbench (using an Automation PC with SG4 PLC) but fails with a constant red LED error when installed in the machine (using an IP161 SG3 PLC). The issue was resolved by replacing the drive. Jaroslav Kovar suggests the root cause is likely hardware-related, potentially involving the drive, the AC114 CAN card, or cabling, and recommends component swapping to isolate the fault. Alexander Hefner offers a theoretical explanation, noting the difference between the SG4 testbench and SG3 machine PLCs. He hypothesizes that insufficient memory on the SG3 PLC might prevent the ACP10 motion module from being spooled to the drive, causing a version mismatch or “deadlock” if the drive’s EEPROM version does not align with the PLC’s requirements.

Spyros confirms that the CAN card and cable were not replaced and that swapping the drive’s position did not help, reinforcing that the original drive itself was defective. He clarifies in post 7 that the new drive came without interface cards, meaning the original CAN and resolver cards were reused. Jaroslav advises that since the problem is solved, further diagnostic time may not be worth the cost, suggesting repair or disposal of the faulty unit. Alexander provides a procedural suggestion for future reference: identify the ACP10 versions in the IP161 project, replicate them on the testbench, and attempt to force a firmware upgrade on the drive to ensure compatibility before installation.