CPx68x Power Supply Diagnostic

I would like to obtain detailed information regarding the diagnostic data point StatusInput01 for the X20 PLC. Specifically, I need to understand how this data point is generated and which states it monitors.

Unfortunately, the information provided across various sources is inconsistent and lacks sufficient detail.

  • In the AS-Help documentation, StatusInput01 is listed under “General controller data points,” with the description simply stating: “Supply voltage outside valid range.”
  • In Automation Studio itself, it is labeled as “I/O supply voltage warning.”
  • According to the data sheet, a double-flash of the red error LED indicates one of the following conditions: LED status indicators for the integrated power supply unit
    • The X2X Link supply from the power supply unit is overloaded.
    • The I/O supply voltage is too low.
    • The input voltage for the X2X Link supply is too low.

Does anyone know exactly which supply voltage is being monitored, and what the specific thresholds are?

Many Thanks!

Hi, I was searching for tresholds for this CPU series and I have not found it. So I can only guess based on what is in documentation for other X20 modules.


I asked AI to do summary based on sources I have found

For CPx68x, StatusInput01 should be interpreted as a combined power-supply warning flag, not as one single dedicated voltage channel.

According to the CPx68x documentation, this warning can be caused by one of these conditions (same group as the red LED double-flash):

  1. X2X Link power supply overload
  2. I/O supply voltage too low
  3. Input voltage for the X2X Link power supply too low

So the different labels (“Supply voltage outside valid range” vs. “I/O supply voltage warning”) are simplified views of the same aggregated diagnostic behavior.

What is explicitly documented for CPx68x:

  • X2X overload indication includes a threshold of > 1.5 A (LED l).

What is not explicitly listed on the CPx68x page:

  • exact undervoltage thresholds (in V) for “I/O supply too low” and “input voltage for X2X supply too low”.

For related X20 system modules, documented warning limits are typically:

  • bus supply undervoltage: < 4.7 V
  • I/O supply undervoltage: < 20.4 V

These values are clearly documented for those modules, but for CPx68x the page itself does not state those two undervoltage numbers explicitly.

Sources

Lets see what other colleagues here in Community can tell us about it.