Hello,
I migrated from AS4 to AS6.7.
I used my program just with ArSim and it worked without a problem, but now I wanted to test it on an APC3100.
But it just starts into the Diagnostic mode.
Here is the Logger: I would start by getting rid of Error 8015
Since the Logger and AS-Help don’t give any decent information, I kindly ask for an idea to solve this problem:
Here is the AS-Help documentation:
Hi @Toby_Herbst ,
Error 30257 is interesting too:
Can you try to create a new configuration in AS 6.7 with just your APC3100? On the new configuration, on the first step don’t add powerlink card, don’t add any task and for timing just select CPU Timer:
If that works, as second step add the powerlink interface card and select for timing the powerlink:
@Note: As you see on my screenshots above I’m using APC3100 with AS 6.7.1.5 (with Hypervisor on my case) and no issue.
Ciao
Valerio
Hello, thanks for the reply.
Just a quick note:
I did an offline installation with a CF card reader and I only had Error 8015.
But if I do an initial installation, this error comes back.
Hi Toby,
As you know, we don’t ask for the project file in the Community since it requires a deep investigation. However, I checked our database and found three similar cases. In all of them, our local support team found specific issues within the project files.
Because of this, I highly recommend contacting our local support team in Germany. They can thoroughly review all of your settings and attempt to reproduce the issue using your specific hardware in their office.
Ciao
Valerio
Hi,
I agree to Valerio’s suggestion, please contact local support.
I think the errors 8015 are “just” follow-up errors as tasks / libraries cannot be installed in diagnostic mode.
The root cause is linked to 30257, there’s some issue identifying or parametrizing then POWERLINK interface on SL2 → support should start investigation there… if the hardware worked / works before with the AS4 project, I assume that there’s something invalid / broken in the configuration files / the project structure… so support will possibly need your project to investigate further.
Best regards!
I think I found the problem:
After I changed the Timer to CPU-Timer, I significantly reduced the errors (no 8015 Error left), and it showed now:
-
The Powerlink Module was configured as a 5ACCIF04.FPLK-000 → But a 5AC901.IPLK-00 was plugged.
-
This caused wrong timing, which created these errors. After I configured the right module and adjusted the Configuration for Timing and Memory, I solved almost every error.
-
I just have the following Errors left; I haven’t checked them yet, but they seem easy to fix.
Thank you for the quick response. The adjustment of the Timing really was the clue that helped me solve this issue.