Error no.-1064116219 is encountered in FB MpAlarmXListUI with no entry in logger

I am encountering error -1064116219 randomly in the MpAlarmXListUI function block, which results in no alarm entries being displayed in the alarm list. The issue occurs intermittently without any specific or reproducible pattern and it does not have any entries for this error in the logger.

The project backup was migrated from Automation Studio 4.7 to 6.5. All the recommended steps for alarm config. conversion were followed correctly, including upgrading the mapp Services version sequentially, first to 6.0.0 and then to 6.7.

For further investigation, I am attaching the Logger, System Dump from the simulation for your reference.

System Dump.zip (2.0 MB)

L1.logpkg (238.9 KB)

Hello,

there are some errors in logger which could be related to that:

Hello,

These are error from the task of M_Alarm which is not in the software of the controller that’s why these errors are occurring I don’t think so, they are related to issue I am facing

Yep, you might be right here.
According to Online Help 28719 is from Visual Components.

Did you try to delete and re-connect the mentioned Variables ?

-1064116219: No alarm selected

Maybe the FB just want to tell you did not select an alarm

when you acknowledge or confirm an alarm