How to fix tuning problem when using two Asynchronous-Motors in parallel to one p66

Hi everyone,

I wanted to share a small discovery I made while using two asynchronous motors with a single inverter.

The normal recommendation is to enter the combined current and power of both motors as the motor parameters, using the sum of current and power in the “Nominal current” and “Nominal Power” section of the motor configuration

After that it is time to do the tuning but it will fail most of the time. From experience, tuning signal are not made to handle 2 motors and the values found on the p66 for RSA, LFA, IDA and TTRA will be most of the time weird and not very functionnal.

Some recommand to do the tuning with only one motor but this can also create strange behavior when the second motor is reinstalled.

So what is the solution? Well I discovered that using as tuning parameters the option “Default values (not recommended)” gives the best result in this situation. I would still try the tuning first in case the p66 is capable of finding effective values but if like me you find a particullarly stubborn configuration, it is something to try.

Hope this help.

3 Likes

Any new findings, small or big, help if shared. So thanks for it.