Hi everyone!  
We are using X90CP154.60-S1 series safe PLC for the project. We have created 10 screens to test, monitor and tune the controllers in mappview. On ArSIM it runs properly and has no problems but on PLC it disconnects every 2 minutes and then reconnects. The refresh rate of the values ​​is very slow and there is a delay.  
Any quick response would be appreciated.

 ![Screenshot 2026-06-03 121029](https://europe1.discourse-cdn.com/brcommunity/original/2X/6/6cbfe1412dd5bd649909d3e23b8e048d97cc8c2d.png)

---

<div class="post-metadata">

**Author:** ![alexander.hefner](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/alexander.hefner/32/111_2.png) [@alexander.hefner](https://community.br-automation.com/u/alexander.hefner)\
**Post date:** [June 9, 2026, 1:22pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/2 "2026-06-09T13:22:45Z")

</div>

Hi,

I’m not an mappView expert at all, but I think one reason could be a [high PLC load](https://help.br-automation.com/#/en/4/visualization/mappview/guides/performanceguides/common_softwareguidance/performance_cpuload.html) and / or the mappView software structure, especially if using some low/mid performance PLC.

So I would propose

- first to check with System Diagnostic Manager (SDM) to see some overview of the CPU load → how much is it over time, and are there peaks?
- please have a look into the[hardware guidlines](https://help.br-automation.com/#/en/4/visualization/mappview/guides/performanceguides/common_hardwareguidance.html), section “Guidelines for selecting server hardware” → your PLC type isn’t mentioned there, I would propose to have a look into the column “CPx583”.
- please check the [software guidelines](https://help.br-automation.com/#/en/4/visualization/mappview/guides/performanceguides/common_softwareguidance/performance_software.html) for possible mappView optimizations

Best regards!

---

<div class="post-metadata">

**Author:** ![florent.boissadier](https://avatars.discourse-cdn.com/v4/letter/f/FF8800/32.png) [@florent.boissadier](https://community.br-automation.com/u/florent.boissadier)\
**Post date:** [June 9, 2026, 8:39pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/3 "2026-06-09T20:39:48Z")

</div>

Hi @Saeed_Rostami

As you didn’t mention what’s this client, I supposed it’s your laptop, so we can avoid a low performance client.  
I would agree with Alexander, mappView is use a quite of CPU and memory. As I never used X90CP154.60-S1 PLC, Alexander mentioned the “CPx583” and on those the mappView application and all moving around Alarms, Audit, OPC-UA may cause the PLC to be too low in resources to handle your application.  
A good thing to check is how many active binding you have on the application, use the diagnostic server to check that ([B&R Online Help](https://help.br-automation.com/#/en/6/visualization/mappview/guides/diagnostics/diagnosticpages/diagnosticpage.html)), I already saw on one of my application where I loaded too much bindings on a client and the mappView server couldn’t handle that.

Hope that could help,

Regards,  
Florent

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [June 15, 2026, 8:33am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/4 "2026-06-15T08:33:21Z")

</div>

HI, thanks.  
The CPU load is 70%, while the mappview part is 3% and there are about 100 signals on OPC UA.

I can’t find the CPx583.

I don’t think the problem is with mappview.

---

<div class="post-metadata">

**Author:** ![hobi72](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/hobi72/32/68_2.png) [@hobi72](https://community.br-automation.com/u/hobi72)\
**Post date:** [June 15, 2026, 9:06am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/5 "2026-06-15T09:06:31Z")

</div>

Hi,

I’d suggest two things:

1. Append ?watchdog=0 to the URL of your HMI (e.g. [http://127.0.0.1:81/?watchdog=0](http://127.0.0.1:81/?watchdog=0) ) … If this helps, it indicates that your PLC is not able to respond to “keep alive requests” in time - this would point in the direction of “overload” of the PLC.
2. Look into the logger … are there any suspicious messages?

CHH

---

<div class="post-metadata">

**Author:** ![florent.boissadier](https://avatars.discourse-cdn.com/v4/letter/f/FF8800/32.png) [@florent.boissadier](https://community.br-automation.com/u/florent.boissadier)\
**Post date:** [June 15, 2026, 9:15am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/6 "2026-06-15T09:15:18Z")

</div>

HI @Saeed_Rostami

Another thing to check, as it’s the client that is disconnected, what the network status, a network that a heavy load could be the root cause, I already saw some trouble with some messed up network, like when there is interconnected classic tcp/ip network with the real-time network like powerlink, ethernet/ip etc..

You can try a direct connection between the PLC and the client!

If you have a way to diagnose the network between the client and the PLC and check if there is a lot of traffic.

Regards,  
Florent

---

<div class="post-metadata">

**Author:** ![Salvador\_Flores](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Salvador\_Flores](https://community.br-automation.com/u/Salvador_Flores)\
**Post date:** [June 17, 2026, 3:38pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/7 "2026-06-17T15:38:58Z")

</div>

Hello @Saeed_Rostami

I recently found the same issue in one of my application, but I was using a Power Panel C50. Here are some advices to help you keeping your server connection:

- Check your Time sincronization between Server an Client
- If you have an Alarm List or Audit List, try to clear their entries. a few weeks ago had the same issue and then after deleting the alarm list (195 pages) the conection remains after that, before that the connection failed when I change to my page Alarms, so I deleted them using my PC, maybe the entries were using too much memory of the CPU.
- Update your mapp view version.

I hope you find them helpful.

---

<div class="post-metadata">

**Author:** ![valerio.manenti](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/valerio.manenti/32/11712_2.png) [@valerio.manenti](https://community.br-automation.com/u/valerio.manenti)\
**Post date:** [June 17, 2026, 3:48pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/8 "2026-06-17T15:48:59Z")

</div>

Thank you @Salvador_Flores for sharing the cause of your issue.  
I never generated 195 pages of alarms during my internal tests 🙂

Ciao  
Valerio

---

<div class="post-metadata">

**Author:** ![florent.boissadier](https://avatars.discourse-cdn.com/v4/letter/f/FF8800/32.png) [@florent.boissadier](https://community.br-automation.com/u/florent.boissadier)\
**Post date:** [June 19, 2026, 12:36am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/9 "2026-06-19T00:36:28Z")

</div>

> [@Salvador\_Flores](#):
>
> - If you have an Alarm List or Audit List, try to clear their entries. a few weeks ago had the same issue and then after deleting the alarm list (195 pages) the conection remains after that, before that the connection failed when I change to my page Alarms, so I deleted them using my PC, maybe the entries were using too much memory of the CPU.

From my point of view for the alarm, the PLC sended the data but the CPU of the C50 was too busy to handle it so, the client didn’t respond in time to ping-pong request of the PLC, so the PLC close the connection

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [June 23, 2026, 1:11pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/10 "2026-06-23T13:11:06Z")

</div>

We are developing in the lab and are always in direct connection with the PLC.

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [June 23, 2026, 1:12pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/11 "2026-06-23T13:12:54Z")

</div>

2.no there are not any suspicious messages. all things are fine!

1.I have a test on Thursday.

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [June 23, 2026, 1:15pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/12 "2026-06-23T13:15:12Z")

</div>

Thanks Salvador:  
Time sincronization is ok!  
No I do not have Alarm List or Audit List!  
mapp viewis updated!

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [June 23, 2026, 1:19pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/13 "2026-06-23T13:19:32Z")

</div>

The problem still persists. We also have a private consultant from BNR. He has proposed a solution to divide the program into two parts and… we have not tested it yet. The pages part is supposed to be run on the laptop and be in simulation and then a connection to the PLC and get the data from the PLC.

---

<div class="post-metadata">

**Author:** ![florent.boissadier](https://avatars.discourse-cdn.com/v4/letter/f/FF8800/32.png) [@florent.boissadier](https://community.br-automation.com/u/florent.boissadier)\
**Post date:** [June 23, 2026, 1:47pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/14 "2026-06-23T13:47:33Z")

</div>

Did you check the mappView diagnostic server to see how many active bindings you want when the connection is closed?

---

<div class="post-metadata">

**Author:** ![kovarj](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/kovarj/32/537_2.png) [@kovarj](https://community.br-automation.com/u/kovarj)\
**Post date:** [July 20, 2026, 9:14am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/15 "2026-07-20T09:14:39Z")

</div>

HI @Saeed_Rostami is it your issue solved, can you update us?

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [July 27, 2026, 8:20am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/16 "2026-07-27T08:20:44Z")

</div>

Hi, no it isn’t. we are struggling with it.

---

<div class="post-metadata">

**Author:** ![kovarj](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/kovarj/32/537_2.png) [@kovarj](https://community.br-automation.com/u/kovarj)\
**Post date:** [July 27, 2026, 11:27am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/17 "2026-07-27T11:27:24Z")

</div>

The last communication tthere is from 23.june, so are you in connection with support colleagues?

---

<div class="post-metadata">

**Author:** ![Saeed\_Rostami](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Saeed\_Rostami](https://community.br-automation.com/u/Saeed_Rostami)\
**Post date:** [July 27, 2026, 12:38pm UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/18 "2026-07-27T12:38:24Z")

</div>

We talked about it a lot before the summer break. The problem is still not solved, but other solutions have been suggested, many of which are difficult and cumbersome.

---

<div class="post-metadata">

**Author:** ![kovarj](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/kovarj/32/537_2.png) [@kovarj](https://community.br-automation.com/u/kovarj)\
**Post date:** [July 28, 2026, 5:45am UTC](https://community.br-automation.com/t/mappview-disconnecting-from-server/11503/19 "2026-07-28T05:45:17Z")

</div>

ok, please if you find real solution or workaround for your project, would be great if you update us here. Thanks a lot.