# Possibility of changing nominal motor data ACOPOS P66 Inverter at runtime

**URL:** <https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351>\
**Category:** Mechatronics & Motion\
**Tags:** acopos, mapp-motion\
**Created:** [February 26, 2024, 2:30pm UTC](https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351 "2024-02-26T14:30:21Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![c566234](https://avatars.discourse-cdn.com/v4/letter/c/FF8800/32.png) [@c566234](https://community.br-automation.com/u/c566234)\
**Post date:** [February 26, 2024, 2:30pm UTC](https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351/1 "2024-02-26T14:30:22Z")

</div>

Hello,

**Introduction:**  
I use an ACOPOS P66 with Powerlink in my machines. I take **Motion Configuration** with the mapp object of type axis **mappAxis** as the function model for the ACOPOS P66 inverters.

**Question:**  
Is there a way to change the nominal motor data cyclically at runtime?

 ![grafik](https://europe1.discourse-cdn.com/brcommunity/original/2X/1/15af10ec4383069911f13d302a02b61a88b2297f.png)

Thank you very much😊.

Best regards  
Johannes

---

<div class="post-metadata">

**Author:** ![michael.bertsch](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/michael.bertsch/32/239_2.png) [@michael.bertsch](https://community.br-automation.com/u/michael.bertsch)\
**Post date:** [February 27, 2024, 9:14am UTC](https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351/2 "2024-02-27T09:14:04Z")

</div>

Hi,

i think there is no access via the MC\_BR\_ProcessParam or MC\_BR\_ProcessConfig to this values.

The values should be accessible via the asynchron Powerlink Registers.  
[PLK-Register P66](https://help.br-automation.com/#/en/4/hardware%2Facoposinverterp66%2F8i0if108.400-3%2Fkonfiguration.html)

To write these Registers you can use this Library  
[AsEpl - SDO Write](https://help.br-automation.com/#/en/4/libraries%2Fasepl%2Ffbks%2Feplsdowrite.html)

I never did it that way, just give it a try.

Greetings  
Michael

---

<div class="post-metadata">

**Author:** ![c566234](https://avatars.discourse-cdn.com/v4/letter/c/FF8800/32.png) [@c566234](https://community.br-automation.com/u/c566234)\
**Post date:** [February 28, 2024, 9:48am UTC](https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351/3 "2024-02-28T09:48:45Z")

</div>

Hello Michael,

Thank you very much Michael.

I’ll give it a try and report back here in the community.

Best regards  
Johannes

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/brcommunity/original/1X/a202d64f0f03e22a662ed33fbbca6879f1efb794.jpeg) [@system](https://community.br-automation.com/u/system)\
**Post date:** [April 11, 2024, 6:58pm UTC](https://community.br-automation.com/t/possibility-of-changing-nominal-motor-data-acopos-p66-inverter-at-runtime/2351/4 "2024-04-11T18:58:55Z")

</div>

Automatically bumped on April 11, 2024, 6:58pm UTC