# Project transfer issue to the X20CP1382

**URL:** <https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035>\
**Category:** B&R Software & Runtime\
**Tags:** plc\
**Created:** [July 21, 2026, 9:45am UTC](https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035 "2026-07-21T09:45:55Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![LeviStone](https://avatars.discourse-cdn.com/v4/letter/l/FF8800/32.png) [@LeviStone](https://community.br-automation.com/u/LeviStone)\
**Post date:** [July 21, 2026, 9:45am UTC](https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035/1 "2026-07-21T09:45:55Z")

</div>

Hello,

I am Levy, Automation Ingeneer and working for AGROCI in Ivory Coast.

My challenge is, I cannot download a project to the X20CP1382 although I can go online, but I get a message during transfer as " **A connection via ANSL is needed to execute Transfer properly**.

I am using the AS4.3.

 ![Download Issue](https://europe1.discourse-cdn.com/brcommunity/original/2X/9/957d2d46e8b3ee8d1937dd50f74c54889e083ae4.png)

---

<div class="post-metadata">

**Author:** ![alexander.hefner](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/alexander.hefner/32/111_2.png) [@alexander.hefner](https://community.br-automation.com/u/alexander.hefner)\
**Post date:** [July 21, 2026, 10:17am UTC](https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035/2 "2026-07-21T10:17:30Z")

</div>

Hi,

please check out this thread, maybe the solution there is helpful:

> [@A connection via ANLS is needed to execute transfer properly error](https://community.br-automation.com/t/a-connection-via-anls-is-needed-to-execute-transfer-properly-error/5352):
>
> I can log into the PLC online, but I receive this error when making changes and during transmission. A connection via ANLS is required for the transmission to be carried out properly.

Best regards!

---

<div class="post-metadata">

**Author:** ![Shoeb\_Rahman](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@Shoeb\_Rahman](https://community.br-automation.com/u/Shoeb_Rahman)\
**Post date:** [July 21, 2026, 8:20pm UTC](https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035/3 "2026-07-21T20:20:05Z")

</div>

![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/b/b0ff2d5c8289639418b70d119d4ea21e5d305263.png)

Hi Levy

Looks like you are currently connected using the older INA connection instead of ANSL and I can see it at tw places which I have higlighted in the screenshot above.  
For a successfull transfer you will have to disble INA. I would delete the TCPIP you currently have and recreate a new one without a node  
number in the INA column, I believe node number 2 automatically comes up but you can delete it.

---

<div class="post-metadata">

**Author:** ![LeviStone](https://avatars.discourse-cdn.com/v4/letter/l/FF8800/32.png) [@LeviStone](https://community.br-automation.com/u/LeviStone)\
**Post date:** [August 24, 2026, 6:22pm UTC](https://community.br-automation.com/t/project-transfer-issue-to-the-x20cp1382/12035/4 "2026-08-24T18:22:39Z")

</div>

Hello Alexander,

Thanks for the support, for it worked for me 😅 .