Setup: B&R PLC (Automation Studio/APROL), single POWERLINK cable from the CPU to 3x non-manageable 8-port hub (B&R 0AC808), which fans out to 16 independent remote I/O zones (bus controllers X67BC8321.L12), each on its own cable.
Symptom: EthRxCRCError counters on several physically independent zones increase by the exact same amount, in sync, in bursts spaced days/weeks apart.
Ruled out so far:
- POWERLINK address collision (checked in config, none)
- Power supply issue on the segment (checked, no anomaly)
- Process-related EMI (machine idle, no process running for 1 month, bursts still occur)
- Cable is shielded, panels normally grounded
- Nothing special in AR logger
One zone also logged somes EthTxCollision, which per B&R documentation should never happen on POWERLINK and points to either a wiring problem or a non-POWERLINK-capable station on the segment — no such station is knowingly present, and addressing was double-checked.
The hub has no diagnostic/error counters of its own, so I can’t get direct visibility into it. The only diag variables i can check is on X67BC.
Questions:
- Beyond shield continuity/ground potential testing, what would you check next on a passive POWERLINK hub suspected of intermittent corruption with no error counters available?
- Has anyone seen a 0AC808 (or similar passive hub) fail in a way that produces synchronized CRC bursts across all ports rather than a single degraded port?
- Any known failure modes on this hub model worth ruling out specifically?
- Can something be seen with Wireshark ?
Happy to share more logger/trend data if useful.
Thank you for help.
Best regards,
Vincent