Hi,

probably your project tries to connect with obsolete INA protocol and you set an invalid INA node number ‘0’ in your CPU.

You could try to deactivate that: [A connection via ANLS is needed to execute transfer properly error - #4 by Tyler\_Carpenter](https://community.br-automation.com/t/a-connection-via-anls-is-needed-to-execute-transfer-properly-error/5352/4)

---