# What is the difference between X20DC2396-01 and 02 on profibus?

**URL:** <https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445>\
**Category:** Controls & Vision\
**Tags:** fieldbus\
**Created:** [January 14, 2025, 3:18am UTC](https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445 "2025-01-14T03:18:17Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![shenyang.zhou](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@shenyang.zhou](https://community.br-automation.com/u/shenyang.zhou)\
**Post date:** [January 14, 2025, 3:18am UTC](https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445/1 "2025-01-14T03:18:17Z")

</div>

We try to add X20DC2396 module on X20BC0063 when we configure the module on Seimens side we find there are 2 modules what is the difference?

 ![daf70adcac188e9ed483971034f2174f_](https://europe1.discourse-cdn.com/brcommunity/original/2X/0/02c1278d8da4ee9050f83a0178d603f257ea56f8.png)

---

<div class="post-metadata">

**Author:** ![oliver\_D](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/oliver_d/32/257_2.png) [@oliver\_D](https://community.br-automation.com/u/oliver_D)\
**Post date:** [January 14, 2025, 5:54am UTC](https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445/2 "2025-01-14T05:54:08Z")

</div>

> [@shenyang.zhou](#):
>
> X20BC0063

Hello,  
basically different “operating modes”  
Please have a look at the manual  
[PROFIBUS Bus Controller User’s manual | B&R Industrial Automation](https://www.br-automation.com/en/downloads/networks-and-fieldbus-modules/profibus-dp/bus-controllers/profibus-bus-controller-users-manual/)

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/5/585c9f1b20a7d081c9e8d491627a98adb1ac721f.png)

The “C02” offers acyclic transfer of additional registers

---

<div class="post-metadata">

**Author:** ![shenyang.zhou](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@shenyang.zhou](https://community.br-automation.com/u/shenyang.zhou)\
**Post date:** [January 14, 2025, 6:12am UTC](https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445/3 "2025-01-14T06:12:43Z")

</div>

Thanks, so does it mean that the module hardware itself is the same, but I can choose different modes in the Siemens software, that is, I can choose either C01 or C02?

---

<div class="post-metadata">

**Author:** ![oliver\_D](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/oliver_d/32/257_2.png) [@oliver\_D](https://community.br-automation.com/u/oliver_D)\
**Post date:** [January 14, 2025, 6:20am UTC](https://community.br-automation.com/t/what-is-the-difference-between-x20dc2396-01-and-02-on-profibus/5445/4 "2025-01-14T06:20:23Z")

</div>

Correct. The hardware is the same but different or more data is transfered. In your case acyclic data