X20BC008T OPC UA PubSub multicast: subscriber receives only from sources within its /22 subnet?
Hello B&R Community,
We are investigating an OPC UA PubSub UDP/UADP multicast reception issue with an X20BC008T running firmware 1.7.1. The subscriber writes an Int16 value to AnalogOutput01 of an X20AO4622 module.
Setup
  • BC IP address: 192.168.20.155
  • BC subnet mask: 255.255.252.0 (/22); no default gateway configured
  • Publisher: open62541-based application on a Linux ARM64 board
  • Publisher and BC connected on the same Ethernet Layer-2 network, with no router between them
  • Multicast destination: 239.0.0.1:4840
  • Publishing interval: 100 ms; subscriber receive timeout: 400 ms
  • UADP payload length: 22 bytes
Initially, the publisher used source IP 192.168.45.123. The BC subscriber was Active=true, but its Received frame counter did not increase, Dataset timeout kept increasing, and the AO node returned BadDataUnavailable. The AO module reported ModuleOk=true. PublisherId, WriterGroupId, GroupVersion, payload length and configured layout matched the subscriber configuration.
We then performed controlled five-second tests by forwarding the existing publisher’s unchanged UADP payload from temporary IP addresses on the SAME physical Ethernet interface. Both boundary tests used the SAME UDP source port (35511), multicast destination and TTL (1); the operating system generated the UDP/IP headers.
Results
Source IP Datagrams sent Increase in BC Received frame counter AO result
192.168.23.1 61 61 Value updated normally (approximately 13116); timeout counter stopped increasing during reception
192.168.24.1 60 0 BadDataUnavailable; timeout counter continued increasing
The BC’s Invalid frame, Invalid network header and Dataset invalid header counters remained zero in both tests. After stopping the successful test, the AO returned to BadDataUnavailable. A separate short test disabling publisher TX checksum offload did not restore reception from the original source IP.
The observed boundary matches the BC’s configured /22 subnet: 192.168.20.0 through 192.168.23.255. However, we do not yet know the exact reason for this behavior and do not want to assume it is an OPC UA PubSub protocol restriction.
Questions
1. Does X20BC008T firmware intentionally restrict UDP multicast PubSub reception to source IP addresses within its configured local subnet?
2. Is there a source-route/reverse-path validation or source-address filter in the BC network stack that could explain these results, especially when no default gateway is configured?
3. Is a gateway or a specific setting required to receive multicast packets from a different IP subnet even when publisher and subscriber are on the same Layer-2 network?
4. Is this expected behavior, a documented limitation, or a known firmware issue? Which diagnostics or configuration changes would you recommend to verify the cause?
Thank you.
topic pinned for next 24 hours, @Marksun if you do not get any idea there during this time, please reach out to official suppport.