Hello

I am new to B&R, working on my 4th proyect, set of 4 exact same machine, code tested and downloades to first two machine, but the next two

automation can`t find the cpu, cpu is in boot mode, please I need some help.

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/6/682f0d2c277d8a4d20bc90163d5447725a052502.jpeg)

Apreciate your comments, Thank you

---

<div class="post-metadata">

**Author:** ![marcusbnr](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/marcusbnr/32/256_2.png) [@marcusbnr](https://community.br-automation.com/u/marcusbnr)\
**Post date:** [October 21, 2025, 7:55pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/2 "2025-10-21T19:55:35Z")

</div>

I recommend double checking the Ethernet settings in your project as this is what gets transferred to the controller (Physical View → right-click on the Ethernet port)

- If you want the IP address set statically, make sure to change the mode and set an IP address
- If you want to be able to browse for the target, SNMP needs to be activated

You will only be able to connect if your PC is on the same subnet as the PLC, so it would also be a good idea to double check your PC’s Ethernet settings.

It looks like you have an X20CP0484 which does not have removeable memory. Once you have your settings configured correctly, you’ll need to do a USB install to get your project onto the PLC.

If your PLC is stuck in boot mode and you are not able to connect, there may be an issue with something in the project. In this case, it can be helpful to create a new, blank project and install that (after setting the correct IP settings!). This will at least allow you to get online with the target and verify it boots a blank project correctly.

---

<div class="post-metadata">

**Author:** ![SGM](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@SGM](https://community.br-automation.com/u/SGM)\
**Post date:** [October 22, 2025, 3:04pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/3 "2025-10-22T15:04:36Z")

</div>

thank you for the replay,

all the settigs are correct, same project was download in two more plc , and it works fine,

plc is stuck in boot mode, correct,

I did new blank project, still not able to get on line

---

<div class="post-metadata">

**Author:** ![marcusbnr](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/marcusbnr/32/256_2.png) [@marcusbnr](https://community.br-automation.com/u/marcusbnr)\
**Post date:** [October 22, 2025, 3:54pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/4 "2025-10-22T15:54:44Z")

</div>

Ah okay thank you for clarifying. How do you know the PLC is in BOOT mode? Is that showing in Automation Studio, or are you looking at the LEDs?

---

<div class="post-metadata">

**Author:** ![SGM](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@SGM](https://community.br-automation.com/u/SGM)\
**Post date:** [October 22, 2025, 4:58pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/5 "2025-10-22T16:58:52Z")

</div>

looking at the leds,

automation studio does not see the plc

---

<div class="post-metadata">

**Author:** ![marcusbnr](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/marcusbnr/32/256_2.png) [@marcusbnr](https://community.br-automation.com/u/marcusbnr)\
**Post date:** [October 22, 2025, 5:21pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/6 "2025-10-22T17:21:13Z")

</div>

The PLC should show up in the Online → Settings, Browse window in boot mode. It would have an IP address of 0.0.0.0 and you’d be able to connect to it. If that isn’t happening, I’m worried that there may be a hardware problem.

What is the sequence of the LEDs that you see?

---

<div class="post-metadata">

**Author:** ![SGM](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@SGM](https://community.br-automation.com/u/SGM)\
**Post date:** [October 22, 2025, 5:45pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/7 "2025-10-22T17:45:45Z")

</div>

online Settings, does not show any thing,

R/E On Red Steady

RDY/ On yellos steady

the rest of it are off

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/b/b5496c93d8c5515301d2a980c12480eaa328c81a.jpeg)

---

<div class="post-metadata">

**Author:** ![marcusbnr](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/marcusbnr/32/256_2.png) [@marcusbnr](https://community.br-automation.com/u/marcusbnr)\
**Post date:** [October 23, 2025, 2:49pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/8 "2025-10-23T14:49:44Z")

</div>

A solid Red R/E light and a solid yellow RDY/F light could mean BOOT or SERVICE mode. However, the PLC should show in the AS “Browse” window in either case as long as SNMP has been activated in the Ethernet settings. Because it’s not, I think there might be something else going on. If you are not able to even connect with a blank project that has the correct Ethernet settings, this might be a hardware problem.

What are the LEDs on the rest of your I/O slices doing? In the picture, it looks like only one slice is powered and I find this strange. But that may just be the case at the time the picture was taken. Do you have a steady 24 volts going to your X20PS9600 module?

If you are unable to connect after installing a blank project via USB and your rack is powered correctly, I recommend you reach out to your local B&R support team.

---

<div class="post-metadata">

**Author:** ![SGM](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@SGM](https://community.br-automation.com/u/SGM)\
**Post date:** [October 23, 2025, 3:31pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/9 "2025-10-23T15:31:40Z")

</div>

I think something wrong with harware, the strange is two at the same time??

I bought 5 sets, exactly the same parts, 3 out of the 5 work

since I have all my sensor all ready connected to the modules, the LEDs are showing the status of the hardware connected to it, but the r led on each slice are flashing

yes I have 24 volts to X20PS9600,

I been in contact with loaca B&R support team, they were remote connecteed trough my pc, to all plc, I hope they come up with fix soon

thank you so much

---

<div class="post-metadata">

**Author:** ![muehlauer](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/muehlauer/32/7833_2.png) [@muehlauer](https://community.br-automation.com/u/muehlauer)\
**Post date:** [October 24, 2025, 8:24am UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/10 "2025-10-24T08:24:15Z")

</div>

Hi,

did you already check the system module X20BBxx?  
When the wrong system module is in the AS project the CPU wont also not boot.

Best regards,  
Florian

---

<div class="post-metadata">

**Author:** ![omer.alumur](https://dub1.discourse-cdn.com/brcommunity/user_avatar/community.br-automation.com/omer.alumur/32/7383_2.png) [@omer.alumur](https://community.br-automation.com/u/omer.alumur)\
**Post date:** [October 31, 2025, 10:27am UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/11 "2025-10-31T10:27:59Z")

</div>

Hi Saul,

In the _Physical View_ section of your project, please right-click on the Ethernet interface you are using (ETH1 or ETH2) and check the setting as shown in the screenshot I shared. If it is disabled, please enable it and save the changes. After that, close and reopen the project — this may resolve the issue.

Let me know if it works.

 ![image](https://europe1.discourse-cdn.com/brcommunity/original/2X/9/9f71e812e43903e6642d9a6774522c047a1f16e8.png)

---

<div class="post-metadata">

**Author:** ![SGM](https://avatars.discourse-cdn.com/v4/letter/s/FF8800/32.png) [@SGM](https://community.br-automation.com/u/SGM)\
**Post date:** [November 8, 2025, 5:46pm UTC](https://community.br-automation.com/t/x20cp048-download-code-problem/8750/12 "2025-11-08T17:46:21Z")

</div>

Hello Every one,

thank you for all the suppor, I took both cpu with Local B&R office, try to downmoad my lap top, did not work either,

we try with on of their lap top, it did work, was able to download the code, Local B&R he read on the forum, this could help, and it did,

the problem was solved just download with diferent laptp,

thanks for the support

---