I’m currently facing a issue with the Ethercat master module (X20IF10G1_1), mounted on the slot of a X20CP1686X CPU.
Initially it was to startup the communication with some Festo equipments. I had trouble to communicate with them.
I just try to go back to the basics and see what happened with a fresh project, only the CPU and the Ethercat master.
The hardware configuration of the module and of the CPU is the default values (except SDM and ETH config for the CPU), here is the configuration of the Ethercat master:
I kinda suspect some hardware issues with the card, something like the CPU cannot communicate with the Ethercat master?
Unfortunalty I try to understand what’s the “NxPCI Error Timeout channel not ready and run: 0xC0CD00C5” is meaning but I didn’t find what’s the problem.
Did someone already see those kind of issue? Or anyone know a way to get more diagnostic informations?
Sometimes the IF modules are not properly seated, so I would start by unplugging it and plugging it back in to the CPU.
You could also try to see what the diagnostics datapoints in the IO Mapping of the interface report. Automation Help: DTM Master diagnostics datapoints
On this page section Communication_Error includes a link to a description for error codes, unfortunately your code was not listed there.
no ad-hoc idea from my side, but more questions: was the ECAT master already in use with HW/FW versions 1.x.y.z before? (e.g. in the project before you mentioned)
Are any slave stations are already configured in the DTM?
I’m just asking because afaik with HW versions 2.x.y.z, a new ECAT master stack was introduced. And I have absolutely no proof, but “error in configuration database” feels a bit like “misconfiguration” that prevents the module from booting (which also could be an explanation für the weird logger entries)…
As I know it’s the first use of the ECAT master, I’ve configure V2.x.y.z before the first transfer to the CPU.
During my tests I have configure a slave station but I wasn’t able to communicate with it. I’ve also try to downgrade the ECAT master version to 1.x.y.z but same problem.
Does the revision of the ECAT master could be the problem? (mine is C4)
C4 is a actual (newest?) revision, so in my opinion should be more then fine.
And all versions you mentioned are the actual ones (especially HW Upgrade & DTM catalogue)… so as it doesn’t work with an empty projects. I’ve no idea where to put the hands on next to be honest.
I think the best would be reaching out to your local support next.
A quick update, I’m waiting for my local support.
But I’ve try the card on another PLC and it’s the same warning.
I had a spare IF card so I try it and after a rebuild → transfer, I got the same warnings.
Now I’m pretty sure it’s not an hardware problem (or I’m really unlucky )
I finally figure it out by myself (I need to give the feedback to my local support).
In fact the error codes are available in the help but only local (B&R Online Help).
I had some multiple error codes, when you do nothing just an empty project with the card you got the warning in the logger with error: 0xC0D60012 = ERR_ECMV4_IF_CONFIG_NXD_WITHOUT_SLAVES
And the error I had: 0xC0CD006D = ERR_ECMV4_EMC_RX_DESTINATION_EXCEEDS_RX_IMAGE_SIZE
Idk why my original post got the error 0xC0CD006D with the project empty (without slaves declared on the Master).
But after more tests, when you have the complete empty project and after initial installation, the IF card is blinking red and the warning in the logger appears with code 0xC0D60012. So seeing those errors / warnings especially the warning about General fault in device driver, I think I got some troubles. But in fact, the EtherCAT master is in error because you didn’t declared slaves on it.
On my eyes I don’t want that to happen even I can understand that (I’ll make this feedback to my local support).
And for the error code 0xC0CD006D, it was an error in the configuration of the slave in the PDO mapping. I finally use some python to see what my slave config was and I figured it out!
Thanks again for your help!
And if someone got the same warning or blinking led, don’t worry (maybe) it’s just you need to add some slave!