XP152 Software Installation Failure – Errors 8016 and 8027 / IF152 Red Error LED

Dear All,

I am experiencing errors during software installation on B&R 3XP152.60-1 CPUs:

  • 8016: PP not present / referenced system bus module missing.
  • 8027: Incorrect PP type at the given module address or PP number.

The rack contains an XP152 as the main CPU and an IF152 for remote I/O communication. The IF152 error LED remains continuously red.

I have performed the following checks:

  • Tested two IF152 modules; both show the same red error LED in the affected system.
  • Tested these IF152 modules in another rack with a working XP152 system; both operate correctly.
  • Replaced the backplane, with no change.
  • Installed the system libraries on the XP152 first, but the IF152 error LED remains red.
  • Set both modules’ upper and lower switches to 1, as instructed by the installation script.

The application download starts successfully but consistently fails when installing DA_AKT1.BR, as shown in the attached pictures.

I tested two XP152 CPUs: one with OS V1.90 reported error 8016, while another with OS V2.20 reported error 8027. The application documentation specifies OS V1.90.

I am unsure whether these installation errors are directly related to the IF152 being in an error state, or whether a configuration or compatibility issue is involved.

Could you please advise on the likely cause and the recommended checks, particularly regarding the expected PP type, module address/PP number, and IF152 initialization?

Thank you for your assistance.

I pinned the topic, needs someone who has experiences with this old system, maybe @corne.geerts or @Viktor could have some ideas?

This makes me think that parallel processor code is generated and running but the PP is not available.

Nevertheless this is too long agoi that I actually remember to be honest. I have worked once with a parallel processor but this is over 20 years ago

best regards

Oliver

Hello, Thanks a lot, I am at your disposal for further information. By the way, I will do some more test in today, I would share in case of having improvement.

Hello Dear Oliver,

Please see the attachment that is logbook from xp152, As you mention it is not communicating with PP (IF152 is my PP for my current status). As you can see logbook, it is recorded an

“ROOT; PPMAN: Different RPSSW Versions on CPU/PP”, As I can see from the online plc info of xp152 version is V2.20 and IF152 is V1.90. That means I have to downgrade OS of the XP152

from v2.20 to v1.90. I need your support for how to find version os v1.90 for xp152 and an instruction how to install it.

NewLOG_xp152.xlsx (10.2 KB)

Best Regards

Serhat

Hello,

I am sorry to tell but I do not have 1.90 - in general OS versions below 2.00 are no longer available as it seems.

best regards

Oliver