B&R’s X90CP174.48-00 with expansion module X90IF730.04-00 communicates 485 with Modbus-RTU, fault code 65535 alternates with 20220
Error 20220 is timeout, which means that there is most likely some issue with the connection to the device. Either in configuration (wrong nodeid) or cabling.
Automation Help: Error Number 20220
Error 65535 means that the function block is busy.
Automation Help: DRV_mbus error numbers
thank you!thank you!
The variable used in datamod is longer than 31 characters.
Have you tried a shorter variable name?