For a project i need to configure the keys on a 7140 mobile Panel. Neither the B&R Website nor the usermanual are giving me enought information to do so. Also all the tools i can download on the website seem not to support the 7140 mobile panel. Could someone give me a hint on how i can change my key configuration ?
And as Jaroslav mentioned one option is to get them via to OPC UA server on the panel. If you are using VNC mode the keys can be read with the RFB extensions.
hey, thank you for the reply. i did create an globle variable and bound them to one of the keys. But after compiling and sending it to the x20 i do not get any response from the key, means the variable doesnt change its value. can someone tell me where i do the mistake?
If I’m not mistaken IO mapping is using internally OPCUA connection from plc to mobile panel. Mobile panel should not be on service page (OPCUA server is not running in this case) so you should go out of service page. If OPCUA connection is not established, moduleOK is FALSE (what is your state?) and I would expect communication error in Logger (activate communication module for that).
If I’m not mistaken IO mapping is using internally OPCUA connection from plc to mobile panel. Mobile panel should not be on service page (OPCUA server is not running in this case) so you should go out of service page. If OPCUA connection is not established, moduleOK is FALSE (what is your state?) and I would expect communication error in Logger (activate communication module for that).
Hi @c581579 - do you have the information per Jaroslav’s questions?
Hi @c581579 - due to inactivity this post will be marked as solved. If you have any updates or further questions on this topic, please add a reply below!