Hello B&R Community,
Controller Type X20EM1613 controller and Automation Studio Version 6.0.2.177 is used in this project.
IF3 port operating mode is used as ETHERNET and IF3 port is configured as Modbus Slave and as Modbus Master. Modbus Master is working but Modbus Slave is not working.
IF3.MODBUSSLAVE_1 is station ID used for Function Block MBSLWORDPUT. On Execution we have Status Error 37451.
On using IF2.MODBUSSLAVE_1 as Station ID for the same function block , get Status ‘0’ indicating Modbus Salve communication via IF2 port is ok.
Looking forward your response to resolve the issue.
IF3 Setting
FUNCTION BLOCK
Hello Mohamed,
For the powerlink interface use ‘IF3.ETH.MODBUSSLAVE_1’ as station.
@beutert thanks it worked !