Hi everyone,
I’m working with a redundant PLC configuration using 2 × X20CP3686X.
I need to expose approximately 20 PLC variables to a third-party Distech controller via Modbus TCP.
However, when I enable “Use as Modbus Slave” on the Ethernet interface (IF2), Automation Studio displays the following error:
“Use as Modbus slave’ is not supported under a redundant configuration.”
I have a few questions:
- Is Modbus TCP Slave unsupported on redundant CPU configurations?
- Is there any supported workaround, such as binding the Modbus server to a specific CPU interface instead of the Cluster IP?
- I noticed that Modbus TCP Master does not generate the same error. Is Modbus Master fully supported with redundancy and switchover?
- If Modbus TCP Slave is not supported, what is the recommended method for exposing a small number of PLC variables to a third-party BMS in a redundant system? Is OPC UA Server the only officially supported solution?
Any clarification or references to the relevant documentation would be greatly appreciated.
Thank you