OPCUA configuration in APROL Runtime for X20BC008T

Hi,

Having trouble connecting to a standalone OPCUA X20BC008T module via APROL. I have configured the coupler with the IP address, Hostname (used this setup before for previous model X20BC008U). Having trouble understanding some of the required inputs for APROL.

  1. What do I require in the OPC UA node namespace parameter and where do I get it? I assume this is something I can find logging in with UA expert?

In this section I amend the IP address, and the username and password for the coupler, is there anything else required?

  1. Setting up the I/O for the module X2X what information is required? I have the node identifier, Connection IO and data type configured.

If it helps I can post a few shots from my UAexpert, if anyone has some useful documentation or can steer me in the correct direction that would be great.

Thanks Dale

Some Extra screenshots from my UA expert setup

Channel setup

IP

Hostname

User Rights

I think namespace configuration can be the issue, check the documenation.

Hello @Dale_Webb,

As @kovarj suggested, in the Aprol configuration, you have the wrong namespace. In UaExpert, you can see NamespaceIndex=4, which corresponds to OpcUa/BC/io-system/.

For clarity, I am including images from the existing running connection:



Tomas

1 Like

Morning,

Great thanks for the response, I will have a go.

Regards,
Dale

1 Like

Solution,

Changed the Server Certificate Verify Parameter to false.

Thanks for help

Dale Webb

1 Like