I’m attempting to connect my 6PPT30.0702-20B HMI to Automation Studio 6 through ethernet cable connection. The HMI is powered, but it just says “Unable to connect to socket, retrying the connection”. I have an X20CP1685 along with I/O modules that I’m using with this setup. I’ve added the HMI to the system designer, and in the HMI’s configuration menu, I gave it an IP address in the same subnet the X20CP1685 and laptop’s ethernet adapter in addition to giving the HMI the same subnet mask. The HMI, X20CPU and the laptop are all connected together via an ethernet switch.
I also created a VC4 visualization and as far as I can tell I tied the visualization project to the HMI via the HMI’s configuration menu. I can’t seem to be able to send anything to the HMI from Automation Studio, I just get the message “Unable to connect to socket, retrying the connection”. From what I’ve seen, I may need to set up a VNC server as a sort of go between the CPU and the HMI, and I’ve tried that in the HMI’s configuration menu, but it doesn’t seem to be working. I’m fairly new to this, any help on this would be appreciated, and ask whatever questions you need to get the full picture.
I accessed the service page for the T30 and configured it the way you mentioned. I also configured the VNC server on the ETH interface of the CPU module and am now able to see my visualization on the HMI. Thank you very much for your help!