Hello,
I would like to adjust or correctly set the current monitoring in my X90CP174. However, I can’t quite figure out from the help how to interpret the INTEGER value for the current measurement.
Unit of the displayed value?
Hello,
I would like to adjust or correctly set the current monitoring in my X90CP174. However, I can’t quite figure out from the help how to interpret the INTEGER value for the current measurement.
Unit of the displayed value?
Tobias
You can find how it should be interpreted here:
link B&R online help: X90 current measurement INT value
Hope this helps!
Jan
Hi Jan,
thanks for your help. I found this already in the B&R help. I can’t understand what it mean exactly.
For example. I have an value of 4644 as INTEGER Value. How do I calculate it regarding the online help. Maybe you can explain it to me.
1 LSB of the INT value corresponds to 610 µA.?
Hi Tobias,
I’ve never used the X90CP174.
Based on the information in the help section, the calculation for your example is rather simple: 4644*610 µA
That equals 2832840 µA
= 2832.84 mA
= 2.83 A
(2,83 Ampere, with the german decimal seperator )
LSB = least significant bit
For an integer the LSB represents the smallest possible step size. For an integer the step size is always 1 ==> if the integer value increases by 1, the current increases by 610 µA
Hi Björn,
thanks a lot for explaining! Now I understand it.
Regards
Tobias