11022 ANSL Communication connection aborted

After rebuilding code I tried several download code to the plc and I failed. Finally I removed all parts of the project from CPU tree branch and also I failed. Interesting is that I am able to ping successfully this PLC and it is still in online status in AS. Connection with PLC is rather qood quality.

Hello and welcome to the Community,

11022 means a connection was lost. Check the PLC or PVI logger as suggested in the help.

Hello,

In this situation i normaly restart the PLC and/or the Automation Studio PC. Then continue with normal operation.

Most often occurances after a Rebuild are Pointers which are not correctly reinitialised an result in a PageFault. (Bad User Software)
In this case the Transfer was typicaly successfull and after the Transfer a Service Mode is issued.

A second issue can be that some EXIT Routine could not finished and your PLC is stuck in EXIT.

Is this a Remote Machine or is this a local PLC on your Desk?
Is a Restart possible?

Greetings
Michael