A connection via ANLS is needed to execute transfer properly error

I can log into the PLC online, but I receive this error when making changes and during transmission. A connection via ANLS is required for the transmission to be carried out properly.

You should have already set up an ANSL connection. This is actually the modern connection if you are using a current CPU and a current Automation Runtime.

Presumably the connection simply breaks off when you transfer your project. There are of course a number of errors that are possible. The reason for the termination should also be described in the logbook. Probably a page fault or a cycle time violation ?

mappMotion also requires special download settings

see Mapp Download Behaviour

Are we talking about a real PLC or an ArSim? In the latter case, it is easier to use an ‘offline’ project installation.

Dear Administrator, I did these, yes, PC PVI Manager is shutting down.

image
Try adding /INA=0 to the Extra CPU settings in the online settings view. This column may need to be added to the view. This setting will force the connection to be ANSL instead of INA. Restarting PVI and/or your computer may fix it temporarily but this modification will make sure it will not happen again on that connection.