Hello Robert,
I’m going to give this my best try to explain, and I’m pretty sure this is accurate. [Corrected for accuracy]
If the X20AT module is operating at 25 C, then the equation for the accuracy of the module only is as follows:
+/- Accuracy = (MeasuredValue * Gain) + (FullMeasurementRange * Offset)
For the X20AT4222, operating at 25 C, and reading a PT100 with a value of 80 C, I get the following:
Accuracy = (80 * 0.00037) + (1050 * 0.000015)
Accuracy = +/- 0.04535 C
The Measured Value and Full Measurement Range are in the units provided by the module, and changes with the configuration of the module:
- Resistance measurement, 4500 Ohms. Full Measurement Range = 4500 Ohms.
- Resistance measurement, 2250 Ohms. Full Measurement Range = 2250 Ohms.
- RTD measurement, -200 to 850 C. Full Measurement Range = 1050 C.
If the module is not operating at 25 C, then the equation expands slightly.
+/- Accuracy = MeasuredValue * (Gain + GainDrift * (ModuleTemp-25)) + FullMeasurementRange * (Offset + OffsetDrift * (ModuleTemp-25))
Note that this only takes into account the module accuracy, and not the sensor, or cable resistance to the RTD.
Best regards,
Austin