ACOPOS Error 41061

Hi, I have a question from a customer regarding the error number 41061. The error occurs on a double ACOPOS multi.

The question is if the error / warning relates to the entire drive, or just one of the two output stages?

Hi,
there is no maximum sum current per module given with ACOPOSmulti so this error must be a channel error.
41061 is triggered when LOAD_CONT_CURR exceeds 95%. Only VCTRL_I1 and VCTRL_I2 are used for calculation (s. GUID c9af4d7e-41a1-4b5e-a40f-320dd25f2749)

if it were an overload of the entire module, it should be a warning regarding the power (41095)
As far as I know, this only exists in the P3.

1 Like

Hello Patric,
this warning only relates to the output state it was reported on (I have also asked a drive firmware developer about this to make sure :wink: )
A detailed description how the continuous current load is calculated can be found here: Continuous current load

1 Like