Hello everyone,
The issue has been resolved with the help of the local B&R service team, and I would like to share the solution here in case it helps others.
If you are using one 8BVF and one 8BVR, the settings can remain at their default values.
The resistance values mentioned earlier apply when two 8BVF units are connected in parallel together with one 8BVR.
In general, the configuration should be adjusted according to the number of filters and shock coils in the system. Since I don’t know the exact number of 8BVF and 8BVR units in your setup, you should refer to the datasheet and enter the corresponding values manually.
You can find the relevant information in the datasheet starting from page 765.
I hope this helps anyone facing a similar issue.