i have a problem with AcoposMulti. Several drives, but three of them sporadically get Error 6055 Holding Brake signal to low. Happens nearly every time after startup and then serveral times a day.
We checked parameters, no issues.
We checked wiring in case of emc problems, not able to find any cause. No other Machines running next to ours.
Has someone ever had a similar problem or any idea what to check?
(AS 4.12 with ACP10 5.24)
best regards
A detailed description of this error number can be found here:
Error 6055
Please check “Cause and remedy”.
If that does not help, please contact your local B&R office for support.
Hi Michael,
I had a similar problem but on a three-axis acopos p3. There were several such ACOPOS in my configuration. The holding brake is powered by the 24 VDC power supply of ACOPOS. When we connected the problematic ACOPOS to another 24V source (circuit breaker), the problem with the brake stopped.
Hi and thanks for this hint. We found exactly the same solution. External 24V power supply needed.