ARWin Showing Run, But X20(c)BC0083 has blinking S/E Led

Good day,

On one of the vessels we have a problem with stopped plc X20(c)BC0083. I have checked the ARWin software and the state is in Run. Also have tried to reboot the entire system - plc + PC, but the problem remains the same. No data coming in or out to the Monitoring system. Ethernet connection is active. On all other modules we have a blinking r or S led.

Did anyone had the same problem before?

System was running normally 2 weeks ago.

Hello,

X20BC0083 isn’t a PLC but the bus controller. What is the status of the S/E LED? There should be an X20PS module next to the X20BC0083. How about its status LEDs?

There Pavel, thank you clarifying that.

The status on X20BC0083 - S/E blinking and L/A IF2 blinking.

The module next to it is X20PS9400 which has the R led solid on.

Thank you.

So it means Mode STOPPED, exactly what you’re describing.

Is there something in the Console tab of the ARwin Startup window?

Where is X20BC0083 connected to? I believe it should be some interface card plugged into the HW where ARwin runs.