Here are some notes which could be helpfull if you work with SfDomain
- How to create a List of SafeApplication, SafeCommissioning on CF
- SfDomainConnect
- SfDomainTransfer
- SfDomainCompletion
- SfDomainExchange
- SafeOptions
6.1 SfDomainLoadSafeOptions
6.2 SfDomainGetSafeOptionXXX
6.3 SfDomainSetSafeOptionXXX
6.4 SfDomainSaveSafeOptions
6.5 Backup of modified Commissioning Files
1. How to create a List of SafeApplication, SafeCommissioning on CF
You can create a List of the Files from the CF-Card by using the DirRead from FileIO Library.
FileHandling.DirRead.pDevice := ADR('CFSafety');
FileHandling.DirRead.pPath := ADR('SafeCommissioning');
FileHandling.DirRead.option := fiFILE;
FileHandling.DirRead.pData := ADR(SafeDomain.DirReadData);
FileHandling.DirRead.data_len := SIZEOF(SafeDomain.DirReadData);
FileHandling.DirRead.entry := 0;
FileHandling.DirRead.enable := 0;
The Files are stored on the C-Partition of the CF-Card
C:\ADDONS\DATA\Safety\SafeApplication
C:\ADDONS\DATA\Safety\SafeCommissioning
Definition of FileDevice
The File Device needed for the Functionblock can be created by PLC-Configuration or via DevLink-Functionblock.
2. SfDomainConnect
EXIT-Task
The SfDomainConnect opens a connection to the SafePLCand is locking operation via other Safety-Services such as the Default HMI. In case of a Transfer of the Application the connection should be relesed.
REPEAT
// Disconnect from SafeDomain
Fb.Connect.Enable := 0;
Fb.Connect.SfDomain := SafeDomainAdr;
Fb.Connect();
UNTIL ((Fb.Connect.Busy = 0 AND Fb.Connect.Active = 0))
END_REPEAT
3. SfDomainTransfer
Progressbar
![]()
The Functionblock “SfDomainTransfer” is using its “StatusID” Output to show different states of the Transfer. It can be combined with the “Progress” Output which showes Values from 0 to 100. If you don’t wan’t to see your Progressbar running serveral times from 0 to 100 you must combine both Values to create a longer Progresbar from 0..700.
Fb.Transfer(Execute := 1);
// Progress Update for Hmi
CASE Fb.Transfer.StatusID OF
sfDOM_INF_TRAN_DATA: SafeDomain.Transfer.ProgressStep := 1;
sfDOM_INF_TRAN_VALIDAPP: SafeDomain.Transfer.ProgressStep := 2;
sfDOM_INF_TRAN_DOWNAPP: SafeDomain.Transfer.ProgressStep := 3;
sfDOM_INF_TRAN_VALIDCOMM: SafeDomain.Transfer.ProgressStep := 4;
sfDOM_INF_TRAN_DOWNCOMM: SafeDomain.Transfer.ProgressStep := 5;
sfDOM_INF_VALID_TABLES: SafeDomain.Transfer.ProgressStep := 6;
ELSE SafeDomain.Transfer.ProgressStep := 0;
END_CASE
SafeDomain.Transfer.ProgressValue := Fb.Transfer.Progress +
(SafeDomain.Transfer.ProgressStep * 100);
// As there are some gaps with StatusID 0 in between we only update the values if they
increase
IF SafeDomain.Transfer.ProgressValue > SfDomain.Transfer.ProgressValue THEN
SfDomain.Transfer.ProgressValue := SafeDomain.Transfer.ProgressValue;
END_IF
IF SafeDomain.Transfer.ProgressStep > SfDomain.Transfer.ProgressStep THEN
SfDomain.Transfer.ProgressStep := SafeDomain.Transfer.ProgressStep;
END_IF
After the transfer has finished the SafePLC will make a Restart. Considering this it makes sens to add a additional Step via the Application to show the progressbar for a longer time. Once the Progressbar is finished the SafePLC has had allready some time for its restart.
Fb.TONWait(IN:=1);
// Progress Update for Hmi (no StatusIDs)
SfDomain.Transfer.ProgressStep := 7;
SfDomain.Transfer.ProgressValue := SfDomain.Transfer.ProgressStep * 100 +
REAL_TO_UDINT(TIME_TO_REAL(Fb.TONWait.ET) / TIME_TO_REAL(Fb.TONWait.PT) * 100);
IF Fb.TONWait.Q THEN
// Reset Timer
Fb.TONWait(IN:=0);
// Next Step
SafeDomain.Step.Redo := 1;
SafeDomain.Step.Step := TSafe_SFDOMAIN_STEP_TRANSFER_D0;
END_IF
The Texts for the Visu can be created like this.
4. SfDomainCompletion
Progressbar
![]()
The Functionblock “SfDomainCompletion” is using its “StatusID” Output to show different states of the Transfer. It can be combined with the “Progress” Output which showes Values from 0 to 100. If you don’t wan’t to see your Progressbar running serveral times from 0 to 100 you must combine both Values to create a longer Progresbar from 0..400.
Fb.Completion(Execute := 1);
// Progress Update for Hmi
CASE Fb.Completion.StatusID OF
sfDOM_INF_COMP_APP: SafeDomain.Completion.ProgressStep := 1;
sfDOM_INF_COMP_COMM: SafeDomain.Completion.ProgressStep := 2;
sfDOM_INF_COMP_SETUPMODE: SafeDomain.Completion.ProgressStep := 3;
END_CASE
SafeDomain.Completion.ProgressValue := (SafeDomain.Completion.ProgressStep * 100);
IF SafeDomain.Completion.ProgressValue > SfDomain.Completion.ProgressValue THEN
SfDomain.Completion.ProgressValue := SafeDomain.Completion.ProgressValue;
END_IF
IF SafeDomain.Completion.ProgressStep > SfDomain.Completion.ProgressStep THEN
SfDomain.Completion.ProgressStep := SafeDomain.Completion.ProgressStep;
END_IF
After the completition has finished the SafePLC will make a Restart. Considering this it makes sens to add a additional Step via the Application to show the progressbar for a longer time. Once the Progressbar is finished the SafePLC has had allready some time for its restart.
Fb.TONWait(IN:=1);
// Progress Update for Hmi (no StatusIDs)
SfDomain.Completion.ProgressStep := 4;
SfDomain.Completion.ProgressValue := SfDomain.Completion.ProgressStep * 100 +
REAL_TO_UDINT(TIME_TO_REAL(Fb.TONWait.ET) / TIME_TO_REAL(Fb.TONWait.PT) * 100);
IF Fb.TONWait.Q THEN
// Reset Timer
Fb.TONWait(IN:=0);
// Next Step
SafeDomain.Step.Redo := 1;
SafeDomain.Step.Step := TSafe_SFDOMAIN_STEP_COMPLETE_D0;
END_IF
The Texts for the Visu can be created like this.
5. SfDomainExchange
Progressbar
![]()
The Functionblock “SfDomainExchange” is using its “StatusID” Output to show different states of the Transfer. It can be combined with the “Progress” Output which showes Values from 0 to 100. If you don’t wan’t to see your Progressbar running serveral times from 0 to 100 you must combine both Values to create a longer Progresbar from 0..200.
Fb.Exchange(Execute := 1);
// Progress Update for Hmi (no StatusIDs)
SfDomain.Exchange.ProgressStep := 1;
SfDomain.Exchange.ProgressValue := (SfDomain.Exchange.ProgressStep * 100) + 50;
After the exchange has finished the SafePLC will make a Restart. Considering this it makes sens to add a additional Step via the Application to show the progressbar for a longer time. Once the Progressbar is finished the SafePLC has had allready some time for its restart.
Fb.TONWait(IN:=1);
// Progress Update for Hmi (no StatusIDs)
SfDomain.Exchange.ProgressStep := 2;
SfDomain.Exchange.ProgressValue := SfDomain.Exchange.ProgressStep * 100 +
REAL_TO_UDINT((TIME_TO_REAL(Fb.TONWait.ET) / TIME_TO_REAL(Fb.TONWait.PT)) * 100);
IF Fb.TONWait.Q THEN
// Reset Timer
Fb.TONWait(IN:=0);
// Reset Progress
SfDomain.Exchange.ProgressStep := 0;
SfDomain.Exchange.ProgressValue := 0;
// Next Step
SafeDomain.Step.Redo := 1;
SafeDomain.Step.Step := TSafe_SFDOMAIN_STEP_SEQ;
END_IF
The Texts for the Visu can be created like this.
6. SafeOptions
SafeOption ID
Die SafeOptionID is required to work with the Functionblocks of the SafeDomain-Library in regards to Safe Commissioning Options.
SafeDesigner
This SafeOptionID can be found in the SafeCommissioning File in SafeDesigner
Automation Studio
This SafeOptionID can be found in the SafeCommissioning File in Automation Studio.
If you open the Commissioning File with a Texteditor you can see the values in the xml-File.
Automation Studio Hilfe
In the Automation Studio Help you can find a Description for the Syntax of the SafeOptionID.
6.1 SfDomainLoadSafeOptions
If the SafeDomain gets disconnected (SfDomainConnect.Active=FALSE), after you loaded the SafeOptions with the Functionblock “SfDomainLoadSafeOptions”, the data is discard in memory. After the next Connect you have to reload the Data from the OptionsFile before you can conntinue editing.
6.2 SfDomainGetSafeOptionXXX
If a SafeOptionID is marked as Visible=FALSE in the Commissioning File. You will get this error from the Functionblock, if you try to access it.
6.3 SfDomainSetSafeOptionXXX
If a SafeOptionID is marked as ReadOnly=TRUE in the Commissioning File. You will get this error from the Functionblock if you try to access it.
6.4 SfDomainSaveSafeOptions
- The CRC will change on every Save-Command. This is due to the fact that there is a timestamp in the file and it will change during Save-Command.
- It is possible to use a different name than the loaded file had. “Save As” is possible, it will create a new File on the CF-Card.
- You need at least one Commissioning file which is on the CF-Card to use the Save-Command, becuase you have to Load a File in advance. If there is no File Loaded you get this error message.
6.5 Backup of modified Commissioning Files
With the FileCopy Function from FileIO-Library you can Copy the Commissioning files from the PLC to an external Storage. This can be used to create an Im-/Export on the PLC.
There are some hints about writing to the c-Partition in the AS-Help. But it is still possible.
File Copy Beispielaufruf
// FileCopy
Fb.FileCopy.pSrcDev := ADR('CFSafety');
Fb.FileCopy.pSrc := ADR('SafeCommissioning/SCFile.sfopt');
Fb.FileCopy.pDestDev := ADR('Backup');
Fb.FileCopy.pDest := ADR('SCFile_Backup.sfopt');
Fb.FileCopy.option := fiOVERWRITE;
Fb.FileCopy(enable := 0);