Good morning @mohsen.bashiri ,
If the ACOPOSinverter is operated on a B&R controller (which is the recommended method), then all the controller parameters are known to the PLC and stored on its flash.
A fresh ACOPOSinverter connected to this PLC would be automatically set up via network.
If the ACOPOSinverter instead is operated stand-alone, it is possible to save/load the parameters in the optional graphic display (Load/Save As).
Regards,