Is it possible to see the channel type setting from analog IO (like 0-10V/ 4-20 mA or 0-20 mA) via the SDM interface? Or are there other options to see the channel type setting without having Automation Studio available?
Hi,
Im note sure about the SDM, but if your Inputs are already Connected, you can see the difference between “current” and “voltage” by looking at the wiring.
You can see the configuration if you open the “*.hw” File in an editor (i.e.: NotePad++)
If there is anything else configured than “±10V” there is an Entry for the corresponding Channel
The *hw File is located in your Projectfolder in “Physical/#YourConfigrationName#/Hardware.hw”
In response to the question about the SDM, it does not generally contain the configuration register information. So, you can’t use it to identify the configuration of the channel.
Hello Guys,
Thank you for your responses.
The point is that our test engineers come to a conclusion that some AI IO is not functioning properly in a physical system.
- They check the wiring, this is correct according to the electrical scheme.
- Next thing they want to check if the IO configuration is also ok. Whats not in this case, because it is configured 0-10V while it had to be 4-20 mA. But they can’t figure this out wouthout asking the software team to check this via Automation Studio
I wondered if there is a way for our test engineers to check this themselves, but doubt there is.
Hi,
the configuration of a analog input / output is set via the “ConfigOutput02” channel, which is a acyclic write-only register. Because of that, it’s not possible to read it back from the hardware, and can’t be shown in SDM or in own programs.
In addition some more general information about hardware channels / registers:
To figure out which information can be accessed (read or write or both) by own software, the register documentation could help. It can be found in the hardware section of Automation Help, for example here for X20AI4622
Hi @c567215 ,
It looks like you got some good suggestions from other community members, and it has been a couple of weeks since the last activity on this post. Can you please mark the reply that helped you the most as the solution? Or if you still have open questions on this topic, can you please provide an update?
Jaroslav
I got some good sugestions how to check things but it seems not possible to see (without Automation Studio available) how the Analog module is configured.
That doesn’t solve my issue, but I know the possibilities, thanks for the help!
Hi Gerben @c567215, it is absolutely fine like that. thanks for your summary and I mark it as a solution. hope that you are ok with it