Unable to Ping or Go Online with B&R PLC 4PPC070.0573-20W Despite Being Visible in Browse

Hi,

probably your project tries to connect with obsolete INA protocol and you set an invalid INA node number ‘0’ in your CPU.

You could try to deactivate that: A connection via ANLS is needed to execute transfer properly error - #4 by Tyler_Carpenter