Updating firmware on the X20BC0088
Below are instructions for how to update the firmware on your X20BC0088.
  1. Download the firmware for the bus controller here: Firmware upgrade X20BC0088
  2. Connect to the bus controller’s webserver
  3. Navigate to the page Advanced > BC Firmware Update
  1. Log in using the button in the top right. By default, the username is admin and the password is X20BC0088 (case sensitive).
  2. Use the button to choose the firmware file.
  3. Click start download
  1. Wait until Download progress says 100%, and then click Restart Bus Controller
  1. Verify the successful update by checking the Version Information section on the Adapter Status page.
Using the web server works for newer EtherNet/IP bus controller modules. However, older firmware versions are not compatible with modern web browsers. The classic error signature is that the web page loads, but no values are populated.
If you do not have access to an old Internet Explorer browser, then you can use the following workaround through the ModbusTCP toolbox.
Alternative Method using ModbusTCP Toolbox:
  1. Download the X20BC0088 firmware and extract the .zip file (link below).
    Firmware upgrade X20BC0088 | B&R Industrial Automation
  2. Download, extract, and install the ModbusTCP Toolbox (link below):
    https://www.br-automation.com/en/downloads/control-and-io-systems/x20-system/bus-controller-modules/x20bc0087/modbustcp-toolbox/
  3. Set both dial switches on the X20BC0088 bus controller to point at F (one notch counterclockwise from 0).
  4. Power cycle the X20BC0088 bus controller.
  5. Plug in a network cable from the X20BC0088 to your laptop.
  6. Set your laptop’s IP address to be 192.168.100.100 (subnet mask = 255.255.255.0) on the Ethernet interface connected to the X20BC0088.
  7. Open the ModbusTCP Toolbox software.
  8. Use the top menu item Tools > Firmware Update.
  9. Click Next. Enter 192.168.100.1 as the IP address of the bus controller. Click Next.
  10. Click Select Firmware Folder to select the folder where the firmware was extracted in step 1. Click Update.
  11. Wait for the update to complete.
  12. Power cycle the bus controller to take the new firmware.
Afterwards, you can access and utilize the webserver to continue configuring the bus controller. The ModbusTCP Toolbox is not used for connecting or configuring the EtherNet/IP bus controller, it is only a workaround for updating the firmware to enable the web server to function with current web browsers.
-Austin