ACOPOSmulti 8BVP0880 – Distorted Mains Currents and EMC Issues

Hello everyone,

At OST – Eastern Switzerland University of Applied Sciences, we are currently building a power systems laboratory in which we use several B&R drive components.

Our colleagues from the EMC laboratory have informed us that our installation is causing significant electromagnetic interference, affecting their measurements.

We are using the following components to supply our drive axes:

-Line filter:** 8BVF0880H000.000-1
-Regeneration choke:** 8BVR0880H000.100-2
-Power Supply Module:** 8BVP0880HW00.008-1

To investigate the issue, I measured the three-phase mains currents at two different locations:

  1. On the grid side, before the line filter (8BVF).

2. Between the line filter (8BVF) and the regeneration choke (8BVR).

As shown in the oscilloscope screenshot, the measured currents are heavily distorted. According to the data sheet the THDi< 0.2% and THDu<1%.

During the measurement the power supply module was enabled and in no load condition.

I configured the Power Supply Module in Automation Studio according to the B&R training materials. For controlling the power supply, I use the MPAxisBasic function block.I have not tuned or modified the controller of the Power Supply Module and did not find any information on how to do so.

Does the 8BVP automatically configure its internal current and DC-link voltage controllers or is additional commissioning or controller tuning required?
Are there specific parameters in Automation Studio that could improve the current waveform.

Thank you for your support!

Best regards,
Adrian