quite specific topic, not sure how many people have already done this. Anyone pinned, maybe someone can help you. If you will not get any suggestion today, I think you will need to get in touch with local support.
When you now take a look at the drives manual (sorry for the german screenshots but I did not had much time to investigate further and could only find the german version of the Profinet manaul for this device)you can find what “Standard telegram 1, PZD 2/2 means” (or any other) :
Looking at the above table which shows 4 times “STW” (I would say thats german for “steuerwort” or in english “Controlword”) and 4 times “ZSW” (which could mean “zustandswort” or in english “statusword”)
This would make sense in my opinion as 2x UINT = 4 bytes of Controlword and 4 byte of Statusword
At least this is what I would interpret here
I hope that helps at least a bit to clearify what you need to enter on the “B&R side” and how you can send data to the drive
There is no need for any library as long it is cyclic data which can be attached via variables to the IO datapoints
Last time, I found out that Festo servo drives could be controlled by B&R X20 PLC and they created some Function blocks (libraries) for EtherNet/IP and Modbus communication.