Image is taken from Redundancy for Control System.pdf
I have successfully configured the controller redundancy using two X20CP3685 CPUs. However, I would like to add another X20CP3685 as a controlled node within the same project.
The challenge I’m facing is that Automation Studio does not allow adding a second CPU to the same project.
Could someone advise on how to properly configure this third CPU as a controlled node.
Thanks in advance for your help!
You need to create a new Configuration for your third PLC. So open Configuration view and create a new configuration.
After you have configured your third PLC and one (or many) of its Powerlink interfaces as a controlled node, you can add it to the main configuration as an intelligent controlled node (epl_icn in toolbox).