When i power up the HMI the above sequence of events happen and later the message is displayed “Connection to Server is Lost!”.
Where as when I access mappview via web Browser it works fine.
Please help me to resovle the issue.
Do you know that for this hw is our recommendation to use max 100 widget of class A/B per page? B&R Online Help Watchdog increasing is temporary workaround, no solution from my point of view.
Thanks for the insight, I will try to fix it actually I have to show all the info on a single page, Can i make compound widgets using compound widgets?
You can not count a compound widget as a single widget. You must also count all the individual widgets used within the compound widget. For example, if your compound widget contains an input numeric field, and a button, then this compound widget must be calculated as using 2 widgets.
This table is a recommendation, not a hard limit. It’s something you should consider during visualization development.
There are widgets with higher performance requirements as well as with lower performance requirements.
The number of active bindings per page can be checked using the mappView server diagnostics server
The points that you required to increase WD, along with this table, indicate that you are running your hardware at its limit. Take this into consideration and think about whether you can split your widgets into more pages or to more contents and load them dynamically.