For example, I’ve configured two AI modules and one DO module.
After importing them into 10D1, all of them are displayed as “module 0”. How can I distinguish which mapping channels correspond to which modules?
Hello Shenyang,
Using an X20BC0088 connected over EtherNet/IP to a B&R PLC is an odd choice. POWERLINK provides much better integration for B&R IO and faster update rates.
However, moving forward under this configuration, you can reference the EthernetIP_CPU1.txt file generated during the build of the X20BC0088. It will be located in the ..\Temp\Objects\[ConfigurationName]\[PLC Name]\AsFDOutput\ folder (where you found the eds file).
Within, you will find the per module and per assembly mapping.
-Austin