How to check the corresponding IO mapping of the IO module configured in the BC0088 module?


For example, I’ve configured two AI modules and one DO module.
After importing them into 10D1, all of them are displayed as “module 0”. How can I distinguish which mapping channels correspond to which modules?

Hello Shenyang,

Using an X20BC0088 connected over EtherNet/IP to a B&R PLC is an odd choice. POWERLINK provides much better integration for B&R IO and faster update rates.

However, moving forward under this configuration, you can reference the EthernetIP_CPU1.txt file generated during the build of the X20BC0088. It will be located in the ..\Temp\Objects\[ConfigurationName]\[PLC Name]\AsFDOutput\ folder (where you found the eds file).

Within, you will find the per module and per assembly mapping.

-Austin