Hi @Nishit ,
Few notes:
- Powerlink node number on X20BC0083
In the prj we didn’t change the default number = 1
so you have to configure the same number with 2 switches:
- X20BC0083 I/O mapping, you can monitor the diagnostics variable below (as first step ModuleOk has to be = 1)
Powerlink diagnostics variable for powerlink interface on your CPU
- Regarding Wireshark please check this very helpful post: Diagnosis of POWERLINK networks using Wireshark
Ciao
Valerio