I have a machine that has an ACOPOS-MULTI SAFE, when I try to run it the drive gives an error, but nothing appears in the plc diagnosis, this machine has another safe plc, is there any way to diagnose the DRIVE?
Hello!
You’ll need to provide a little more information.
- ACP10 / mappMotion?
- Sytemdump from the SDM: http://<plc-ip>/sdm
- Logger details from Automation Studio or the SDM
- Network Command Trace from AS or SDM
- LED status information of the drives
Best regards,
Hi Estanislav, have you found solution for your problem? If so, can you share it with us
We didn’t find the root cause of the problem, but I noticed that the cable connection included a connection for the engine brake, but the engine has no brake, I removed the brake cables and the drive returned to normal, I couldn’t see the unit setting .
2 Likes