that’s strange, I don’t know any way to let the CP476 stay in normal mode (RUN/SERV), when the mode/node switches are set to “00”… maybe some hardware issue? I don’t have any other explanation for that.
Alternative to BTL mode for upgrading SG3 AR
Thinking about how to upgrade a SG3 AR without using BOOT mode, I remembered some old knowledge that I’ll document here.
Having a minimum version of AR already installed (I don’t remember this minimum version, I guess it was something around V2.20 or so), it was possible to transfer a operating system also as a “normal” BR module download in RUN mode.
If just the operation system file used for BTL mode (the .s1* file) was available, it has to had packed into a BR-file using some external tool… and Runtime Utility Center 4 also have the possibility
to do that, the RUC command for that is “Generate AR Update module”.
So I was curious and did some tests - I don’t have a CP476, so I can’t test with the exact same PLC that you have, I used a CP474 instead which should be “similar enough” to get some information also about your use-case.
Building the AR SG3 Update module
Unfortunately, I wasn’t able to get this command executed in my Windows 11 environment, I assume the reason is that this command uses some old (maybe 16 Bit based?) code or I’ve had some user rights problems, I haven’t investigated that further.
Instead, I used my WindowsXP VM and some older RUC installed inside there, and built the module.
Transfer
After update module was created inside the VM, I proceeded with my RUC 4 installation on Windows 11 which worked well.
I created a RUC command file that connects to my CP474, deleted the complete memory of it, transferred the update module…
… and executed the PIL (as the module is a big one, the transfer needs some time) …
… and everything worked as expected! After the execution of the PIL was finished, my CP474 was upgraded from V2.30 to V2.35.
In a nutshell
At least if some prerequisites are fulfilled, it’s possible to update a SG3 AR with just having the .s1* file not using BTL mode.
This is nothing new, but I thought it could be helpful documenting it here in our Community.
Best regards!
PS @gConejo,
I additionally created a CP476 V2.35 AR Update module. I’ll send it to you via private message.
Please be aware that I wasn’t able to test this update module of CP476 because of missing hardware! So I can’t guarantee that it works, but I think it should 