X20 CP0482 loose his IP Address

Hello,

I have X20 CP0482 with Automation studio 4. I try to give to my plc an ip address with the software bootp/dhcp server from Rockwell with the option “address from dhcp server” in automation studio. Sometimes that’s not work and sometimes yes. When that’s work, I can’t detect the PLC via the menu “online” “setting” when I scan the network. However, I can transfer the configuration and the program. After this step, I set “ip address manually” when the ip address is stored (a ping command is ok).

But if I switch off the power supply, the ip address is lost and the Led R/E is red. The PLC seems doesn’t keep the IP address. I see the request by wireshark from the plc, the ip address is gave and it lost immediateky, after there is no new request from plc. I find a question in this forum “how to connect to a PLC with an unknown ip address” but this procedure doesn’t work.

I don’t find a similar problem here. Someone can help me please ?

Thanks for your help.

Hello,

If your PLC should be visible in the Online Settings, you have to activate SNMP on the ETH interface.

Hello,

It was desactivated. I’m going to try again tomorrow activating this option.

Thanks.

Hello Pavel,

That’s work ! Perfect ! Many thanks for your help.