X20IF10E1-1 not able to configure a pn/pn coupler (6ES7 158-3AD10-0XA0)

Hi

I’m not able to setup this pn/pn coupler up, using the gsd file.

I am getting this error. under diagnose

image

I seems that the pn coupler are not able to load the configuration, so ip are are not being set.

Do anyone have experience with this setup ???

Hello Soeren,

can you share the GSDML file ?

Regards
Stephan

Yes off course, I’m not allowed to share files yet, but I downloaded it from this link.

PROFINET GSD files : Gateway - ID: 23742537 - Industry Support Siemens

BTW. in the pn coupler we are using a fast connection type, and not rj45.
And the version on the pn coupler are 4.2.

Hello Sören,

in my opinion the PN/PN coupler should work. It is important that you do not insert the ProfiSafe mappings in the configuration. They are not supported. It is best to test the communication with a simple mapping (e.g. 16Byte In and 16ByteOut). This must be entered on both Profinet masters.

Regards
Stephan

The issue has be solved, it issue was that the pn coupler, won’t setup the ip from automation studio remote. So instead I use the proneta software from siemens. And then i also can see more information on the coupler as well.

2 Likes