APC910 - UPS manager error 50

Hello,

I’m using an APC910 in combination with an 2.2Ah UPS (5AC901.UPS-01). The system should shutdown on power loss and after the defined amount the UPS should turn off as well.
The shutdown functionality is not working and after checking the UPS Manager i see that it indicates “Error 50“ on all information tabs:

Can anyone tell me what the cause is of this issue as i cannot find a manual for it?
We’ve checked the wiring and this is correct.

Additional information:

Kind regards,
Jeroen

Hello Jeroen,

Which bios/mtcx is running on the APC910 ?

According to the ADI SDK error 50 = The request is not supported (e.g. because the installed BIOS version is too old).

Hi Job,

Main BIOS Version APCBR8126
MTCX 1.32

Is this a new APC ? Could you test the latest drivers ? ( The ADI 2.4.1 is from okt 2023 )
ADI driver universal | B&R Industrial Automation

Hi, has latest driver solved your issue? can you update us?

Hi Job,

Unfortunately i’m not able to install this ADI driver. Our APC is running on windows 10 Enterprise 2016 LTSB, this driver does not support 2016 LTSB.
Is there also a new ADI driver for the version that we are using?

Hi @Jeroen_Verhofstad , please get in contact with the support of your local B&R office, and when you investigate the solution, please share it with us.