DNA configuration error

Hello guys.
I have some trouble with the configuration of powerlink connection for a 8I86T401500.0P-100 inverter.
Since I don’t have the external display to set the node, I activate the DNA mode.
The line is configure in this way:

5PPC2200_AL02_000 node 240
X20BC0083 node 1 DNA on
8I86T401500.0P-100 node 2 DNA on

If I check the module in SDM, the inverter is always not plugged.

Any suggestion?
Thank you

The cables must be connected like shown in the System Designer.
Also the powerlink master must be defined on DNA Configuration = automatic.
The physical switch of X20BC0083 must be defined as node = 1.

Hi all,
thanks @corne.geerts for suggestion.
I made a mistake, the issue was not related to the DNA configuration.
The issue was due to the motor current parameter being set below the minimum allowed value. This caused the inverter to go into boot loop.
The configuration sheet report 0.1A format, but with my inverter the correct format is 0.01A!
Once I got hold of an external display, I was able to verify that it wasn’t a node issue and I was able to solve the problem.
Thanks again!