Hello,
I am configuring safety communication between two B&R X90CP174.48-S1 controllers using openSAFETY over UDP.
My application requires more than 8 bytes of independent safety data to be transmitted cyclically between the two X90 controllers.
However, in my current openSAFETY over UDP configuration between two X90 controllers, I can only find one SafeDOMAIN Connection, and I cannot find any option to add another connection.
My questions are:
- Is it possible to configure multiple SafeDOMAIN Connections between the same two X90 controllers when using openSAFETY over UDP?
- If yes, where can additional SafeDOMAIN Connections be added or configured in Automation Studio / SafeDESIGNER?
- If multiple SafeDOMAIN Connections are not supported for openSAFETY over UDP, what is the recommended way to cyclically transmit more than 8 bytes of independent safety data between two X90 controllers?
For example, I need to transmit:
- 6 signals of 8 bits each
- 32 signals of 1 bit each
Therefore, the total amount of safety data exceeds 8 bytes.
My environment is:
- Controller: B&R X90CP174.48-S1
- Automation Studio: 4.12.6.106
- SafeDESIGNER: 5.24.1.0
- Communication: openSAFETY over UDP
Thank you for your support.
Hello,
If i have a look in the Datasheet of the Device is must say this looks like a hard limit.
Max. Number of Data 8 Bytes
Max. Number of Links 1
X90CP174.48-S1 | B&R Industrial Automation
Greetings
Michael
Hello,
Thank you for your reply and for pointing out the hardware limitation.
I understand that the X90CP174.48-S1 is limited to 8 bytes of SafeDOMAIN-to-SafeDOMAIN data and one link.
In our application, however, we need to cyclically exchange more than 8 bytes of independent safety-related signals between two X90 controllers.
Is there any recommended B&R solution or architecture for this use case?
For example, is there another way to establish additional safe communication between the two X90 controllers, or is more than 8 bytes of safety data fundamentally not possible with this X90 hardware configuration?
Thank you for your support.
Hi Daisuke:
I had a similar issue with communicating data between the Standard Application and the Safety Application, in transferring data between them.
My solution was to essentially create an asynchronous multiplexer where one of the data values transmitted to the Safety Application was a tag describing the data content. The Safety Application sent back a response to indicate when the data had been read.
I saw approximately a 50 millisecond response end to end from queueing up the data to the Safety Application responding that it had received the data.
I’m not sure if you can do this with Safety UDP, or whether the latency is acceptable; but something along this line would be what I would attempt.
Hi Mike,
Thank you very much for sharing your experience and idea.
I understand your approach of using a tag to identify the data content and an acknowledgement to confirm that the data has been received before transferring the next data.
This is a very interesting idea and gives me another possible approach to consider.
I will continue to investigate whether a similar concept can be applied to my application with Safety UDP.
Thank you again for your helpful suggestion!