As the question really
I have multiple configurations, but the safety i/o and project don’t change
Thanks,
Brian
As the question really
I have multiple configurations, but the safety i/o and project don’t change
Thanks,
Brian
Hi Brian,
I believe this should be possible with a reference to the package from the “main” configuration.
This can be done in the cpu.pkg file like this:
<Object Type="Package" Reference="true">\Physical\ConfigName\PLCName\mappSafety</Object>
Thanks Tobias, I’ll give that a try
I guess that the safe i/o must be identical to work so I’ll copy and paste that
Brian
Hmm, that didn’t work
Added these to software and it looks better. I can open safe designer, download etc.:
![]()
Can’t get the pre-configured HMI to work properly now - it looks to be stuck on a file that I saved yesterday
Safe designer disagrees, as does explorer:
No idea which one mappVIEW is using… I’ll keep digging
Brian
Hello,
After a Compile the SafeApplication is stored as a file in the Configuration View. This files are used while transfer to the PLC
MappView is accessing the Data on the C-Partition of the CF-Card of the PLC.
There is a Folder where the SafeApplication is stored after the Transfer with Automation Studio.
Greetings
Michael Bertsch
Thanks Michael
Found the correct one. I have no idea why an old version is shown when you first connect to the PLC, but browse found it straight away
All the best,
Brian
Marking this as solved by posts 2, 3 and 5