Safety X20SL8101 remains in "No execution"
I have the safety plc which remains in ‘No execution’. In SafeDesigner there are no errors and the modules and FW/Safe KEY are OK. Looking at the device’s diagnostic LED I have this condition:
“Safe communication channel not OK, openSAFETY connection valid problem or
“SafeOSstate!=RUN”
If the SafeLOGIC controller remains in this state for a longer time, parameter
“Default safe data duration” of the “Group: Safety response time default values”
must be checked.”
In the AS logger I have these alarms but I do not understand what the problem is with these devices:
Could it be some parameter regarding communication?
Many thanks
Stefano Marelli
Hi Stefano, welcome to the community!
From the suggestsions in the help of logger message -1073553380 this one looks most promising:
Ensure that the safety project and the project of the target CPU do match.
This means to compile and download the projects in AutomationStudio and SafeDESIGNER.
Hi Roman, thanks for your suggestion. In the end we found that a bus controller was not in operational state due to an electrical problem. Having solved that, the safety plc went into run state.